Wha is a broken neutral and what is the consequence of it
![]() |
Wha is a broken neutral and what is the consequence of it
Where is it broken?
Chuck
An open neutral gives your system no reference for 120v loads. So any 120v loads will be seeing voltages up and down from 0 to 240v depending on how balanced the load is.
240v loads will still see the correct 240v.
An open neutral is NOT a good thing. Why do you ask this?
Just doing sum research on reverse polarity,thanks for the info
I take it your tester showed reverse polarity, and you found an open neutral?
Yes with the reverse polarity!thanks for the response
Once you have the open neutral corrected/connected, tester will show OK.
Information provided by Stanfourtyman is accurate and also applies.
Do you need help finding open neutral?