I looked it up:
Ht = U A dt (1)
where
Ht = heat loss (Btu/hr, W)
U = "U-value" (Btu/hr ft2 oF, W/m2K)
A = wall area (ft2, m2)
dt = temperature difference (oF, K)
1. You were given the total area and from that you can calculate the window area. Subtract the window area from the total area to get the wall area. dT is 10 degrees F. You are given U for the varoius areas. Do the calculation (equation 1) for both areas. That is the total heat loss.
2. a. Figure out the area of the area of the warehouse. Assume each wall is a rectangle and I assume the roof is also a rectangle. Multiply the total area by the maximum permitted area (a fraction you read from your "maximum single-glazed areas" for each of the areas. Subtract each area from the total. The remainder of the area is wall. Perform the heat loss calculation on each of the areas separately. Add all of the heat losses. That will give you the power requirement.
b. Do the same calculation, except use the given U value for the window and rooflights.
This is very straight-forward. Don't make it harder than it really is.