    Can circuit work well if we connect 12A load to 20A circuit?
    Hello:

    I have several equipment which are around 12A. I just can connect them to 20A circuit.

    But I am not sure if circuit will trip well under overload and short circuit.

    I know 15A is perfect.But,I don't have 15A circuit

    Thanks for everybody.
  • Jun 12, 2009, 02:02 PM
    tkrussell
    A 20 amp circuit will work fine with a 12 amp load, no concern needed for short circuit or overcurrent protection of a properly working and installed breaker.
  • Jun 12, 2009, 04:43 PM
    stanfortyman
    The breaker protects the wiring, NOT the equipment.
  • Jun 14, 2009, 08:19 PM
    JZELECTRICAL

    Does that mean we also can connect 12A load to 25A,30A,or bigger circuit?(12A is only load)

    THanks for answer
  • Aug 4, 2010, 06:19 AM
    kryostar

    Yes a 12A load can go on a 15A circuit or 25A.30A breaker you never want the other way around 20A load on a 15A circuit
  • Aug 4, 2010, 06:34 AM
    tkrussell