Reduced Neutral for Subpanel Feeder
Hello,
I am adding a sub-panel for a new cooktop and double wall oven. They are rated 9KW and 7.5KW.
I already have 1" EMT run from my main panel to a good location under the kitchen in the basement (about 40').
I have some wire and a load center on hand that I would like to use if I can, instead of buying more at today's copper prices. I have about 100' of #4 THHN, which is enough for my 2 hots. I also have some #6 THHN and a Siemens 125A, main lug, 4-position load center (E0408ML1125SU).
I'm thinking that per 220.61(B)(1), I can use the #6 wire for my neutral since it will only be serving cooking appliances. Am I correct in applying this code section?
I would be using an 80A breaker for the feeder and a 40A for each appliance in the sub.