  • Jun 7, 2009, 02:58 PM
    engjon510
    AC Wiring issue (Carrier Weathermaker 8000 24v error code)
    I have a Carrier Weathermaker 8000 furnace, which I just had the Control Board changed. Tried turning on the AC and nothing. Get the 24 error code which is 24 volt short. Keeps blowing the 3 amp fuse. Have replaced the wires from the Condenser to the control board. If I remove the wires from the board and turn on the heat, it runs. Turn on the AC with the wires off, fuse blows. Any help would be greatly appreciated!
  • Jun 7, 2009, 03:01 PM
    engjon510

    Oh and I have done a visual on all the control wires and do not see a short.
  • Jun 7, 2009, 04:29 PM
    Joshdta

    Fuse blows with the wire unhooked at the ac unit?
  • Jun 7, 2009, 06:08 PM
    mygirlsdad77

    If fuse blows with wires disconnected from ac unit, it sounds like you have a short in thermostat wires from thermostat to board on furnace. Or, new board was inproperly wired.
  • Jun 7, 2009, 07:28 PM
    T-Top
    Check for a low voltage short inside the A/C unit: Wires going to the high pressure or low pressure switch. A coil that is bad on the contactor will give the same symptom.