    Types of Double Pole Breakers?
    I just installed an appliance that called for a 240v 20amp service. I ran the line and attached a double pole 20 amp breaker (It had two separate throws). The appliance would not work. I installed another 20 amp breaker with a common trip and it runs fine.

    What is the difference?

    I have a Cutler-Hammer BR series box. Both breakers where 20amp double pole breaker for the BR series. What's the deal?
  • Jun 1, 2009, 03:03 PM
    stanfortyman
    The first one you tried was NOT a double-pole breaker. It was a twin, or tandem, breaker.