  • May 29, 2009, 01:46 PM
    mydeadcatmurphy
    How do I wire a clothes dryer?
    In my shop I have a 220 or 240 outlet. Can I use it to run a home style clothes dryer and how do I wire it with out blowing up the dryer?
  • May 29, 2009, 02:15 PM
    bones252100

    Most dryers use 220 VAC although the connection plugs can be different. If your dryer uses 220, then purchase & connect the matching plug for your outlet. If the dryer does use 110 VAC, it is possible to tap off one side of a 220 line to provide 110 but you probably have a 110 receptacle somewhere in the shop. Those lights run off 110 VAC. If rewiring the 220 line is the only option, have a licensed electrician do the installation. 110 volts can kill. 220 volts WILL kill.
  • May 29, 2009, 02:26 PM
    stanfortyman
    A household dryer is a 120/240v appliance, not simply 220. Meaning it requires a neutral along with the two host and ground. It typically requires a 30A circuit run with #10 wire.

    If this is a straight 240v receptacle you have you need to determine if a neutral was run, or just two hots and a ground.
    Also, you need to determine what size wire was run and what size breaker it is one.
  • May 29, 2009, 03:58 PM
    jerro

    Also is it a new dryer or older dryer. This could determine if you need a 3 prong or 4 prong plug to connect to your dryer.
  • May 29, 2009, 04:21 PM
    stanfortyman
    Well if he is re-wiring a circuit to accept the dryer it would need to be 4-wire. It is the circuit that determines 3 or 4 wire, not the dryer.

    In any case an insulated neutral is required.
  • May 29, 2009, 04:57 PM
    Washington1
    Quote:

    Originally Posted by stanfortyman View Post
    Well if he is re-wiring a circuit to accept the dryer it would need to be 4-wire. It is the circuit that determines 3 or 4 wire, not the dryer.

    In any case an insulated neutral is required.

    Exactly!!
  • May 29, 2009, 05:41 PM
    Fr_Chuck

    And since you use the term ( home style) I will assume this is a commercial building, and I will note you don't have any idea what voltage you have.

    Many, if not most commecial buidlings in our area are 208 not 230 VT