Was Told Capacitors (Phase Shifters) Were Running Low and Need to be Replaced?
Thanks to everyone who helped me get my upstairs AC going! My down stairs unit froze up once this year so I had a tech come out to check it. He added some freon to the unit and told me that the unit was in pretty bad shape and this I should consider replacing the whole unit. This AC unit is a Comfortmaker with forced air heat. He said that the condenser in the air handler was rusty (which it is a little rusty). He also said that the phase shifter (capacitor) in that unit was suppose to be putting out 7.5uf but was only putting out 6.1uf and the capacitor or phase shifter in the outside unit was rated to put out 35/3uf but was only putting out 28/2.8uf. He suggested that I replace both for a total cost of $470.00!!
I obviously declined the service. My question is should I replace these capicators or are they fine like they are? Will they cause any problems with the fans or compressor running a little low like they are now? I have seen several of the capacitors on the internet at very reasonable prices, does anyone know of a great place to purchase replacements if I need them?
Thanks in advance!