    Why is my airhandler coil freezing up can you help.
  • May 28, 2009, 01:04 PM
    letmetellu

    There are several reason for the coil to freeze over. So what you hae to do is go down the list to find the cause in your case.

    Dirty Filter-----replace filter.

    Dirty Evaporator coil-------clean coil

    Return air grills blocked-----make sure grills are not blocked.

    Some supply registers closed---open registers

    Freon level in condensing unit is low--charge unit.

    Air handler motor speed is too low---increase speed or change motor.

    These are the reasons that you might find, there are others.
  • May 28, 2009, 05:01 PM
    mikiej52

    Two things can cause icing in the evap section, improper air flow, and low refrigerant charge. Improper air flow can be caused by many things, dirty filters, dirty coils, too many supply vents closed. The motor speed needs to be correct also.
  • May 28, 2009, 07:48 PM
    T-Top
    I'll add some. Restriction at the TXV or piston at the evaporator coil. But I'm going with the low refrigerant level.