    Second floor DWV
    All,

    I have a second floor bath which I am remodeling. There is an existing 3" stack through the roof.

    I have a 2" line from the stack with a 1.5" lav drain and a 1.5" vent to the attic.

    I also have a 2" line from the stack with a 2" shower drain and a 2" vent to the attic.

    I am adding a tub

    My question is:

    Can I drain the tub on the lav line with the 1.5" vent? (I believe it should be a 2" vent)

    Can I drain the tub on the 2" shower line?

    Is there some combination that will work?
  • May 27, 2009, 09:30 AM
    massplumber2008
    Hi Shipswake...

    Drain the tub into the 2" shower drain with the 2" vent. Here, the 2" vent/drain from the shower will be perfect to WET VENT the tub... ;)

    If wet venting isn't allowed in your area then you will need to install a 2" x 1.5" wye into the shower drain (after the 2" vent connection) and run 1.5" over to the tub and then run 1.5" tub vent and connect into another vent at a minimum of 42" off the finish floor.

    I'm betting you can wet vent the tub! Check with any local plumbing inspector and just ask if wet venting a tub with a 2"shower drain/2"vent is OK... it is in most states.

    Let us know if you need more info...

    MARK
  • May 27, 2009, 10:34 AM
    Shipswake
    Quote:

    Originally Posted by massplumber2008 View Post
    Hi Shipswake....

    Drain the tub into the 2" shower drain with the 2" vent. Here, the 2" vent/drain from the shower will be perfect to WET VENT the tub...;)

    If wet venting isn't allowed in your area then you will need to install a 2" x 1.5" wye into the shower drain (after the 2" vent connection) and run 1.5" over to the tub and then run 1.5" tub vent and connect into another vent at a minimum of 42" off the finish floor.

    I'm betting you can wet vent the tub! Check with any local plumbing inspector and just ask if wet venting a tub with a 2"shower drain/2"vent is OK...it is in most states.

    Let us know if you need more info...

    MARK

    Thanks for the reply Mark

    I am also in Ma, so I assume wet venting is OK.
  • May 27, 2009, 02:51 PM
    massplumber2008
    Absolutely OK here...

    Connect into the shower drain... should be all set!