    juron
    Wiring new ceiling light with 2 wall switches.
    Hi! Need help to a simple wiring problem. Just installed a new ceiling light with 2 wall switches. Both fixture bulbs have a black and white wire. The ceiling outlet has 2 red , white and black wires, and a ground. The previous fixture did not use the red wires. I connect the fixture black to the ceiling black wire, and the fixture white to the ceiling white wire. One wall switch does not work at all, and the other wall switch only lights one bulb. Both bulbs are new. Thoughts please! Thanx- juron [email protected]
  • May 26, 2009, 07:19 PM
    hkstroud
    Quote:

    Originally Posted by juron View Post
    2 red , white and black wires, and a ground.

    Does that mean 2 red, 2 black and 2 white?
  • May 27, 2009, 06:45 AM
    juron
    Yes, 2 red that I believe were not used previously, 2 black, 2 white and a ground. Thanks for the reply.
  • May 27, 2009, 07:16 AM
    hkstroud

    One of the white wires will be the neutral. Because the light works, you must have already connected it to the white of the light.

    The black and red wires in the cable with the neutral will be the traveler wires from the first switch.
    In the other cable, two of the wires will be the traveler wires to the second switch. The third wire in that cable will the switch leg returning power from the second switch. The problem is that right now we don't know which is which.

    Pull the second switch (the one that doesn't work). See which wire is connected to the common screw. Connect that wire to the black (hot ) of the light.

    Connect the other two wires in that cable to the red and black wires of the cable from the first switch. It does not matter which connects to the red and which connects to the black.
  • May 27, 2009, 11:07 AM
    juron

    Well, thank you very much! It will be a week or so before I try it as it is at my daughters home.
  • May 27, 2009, 03:36 PM
    juron
    Quote:

    Originally Posted by hkstroud View Post
    One of the white wires will be the neutral. Because the light works, you must have already connected it to the white of the light.

    The black and red wires in the cable with the neutral will be the traveler wires from the first switch.
    In the other cable, two of the wires will be the traveler wires to the second switch. The third wire in that cable will the switch leg returning power from the second switch. The problem is that right now we don't know which is which.

    Pull the second switch (the one that doesn't work). See which wire is connected to the common screw. Connect that wire to the black (hot ) of the light.

    Connect the other two wires in that cable to the red and black wires of the cable from the first switch. It does not matter which connects to the red and which connects to the black.

    A bit more clarification needed please. Does your reply cover 1 or 2 bulbs in my fixture?My fixture has 2 light bulbs, each with a white and black wire. Since 1 fixture bulb lights, this bulb must be connected to the white neutral. Can I connect both white wires from the fixture to the white neutral? Where do I connect both black fixture wires? Thanks again-
  • May 27, 2009, 03:40 PM
    hkstroud

    Both black fixture wires are connected to the hot wire from the common screw of the second switch. Both white fixture wires are connected to the neutral.
  • May 28, 2009, 06:52 AM
    juron
    Thank you:-)) This should solve the problem.
  • Jun 4, 2009, 07:16 AM
    juron
    Quote:

    Originally Posted by juron View Post
    Thank you:-)) This should solve the problem.

    Walla! :-)) Thanks for the help.