Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   AC Compressor will not come on (https://www.askmehelpdesk.com/showthread.php?t=356993)

  • May 23, 2009, 06:42 AM
    km4um
    AC Compressor will not come on
    My AC compressor will not come on. Blower works but not compressor. Breaker is good. How do I check to see if it is getting power? And more importantly, is this something w/o an electrical or HVAC background should attempt?
  • May 23, 2009, 06:54 AM
    Stratmando

    If Compressor Fan is working, then the control wires and contactor is working. May be the Motor.
    If Compressor and compressor Fan don't work, then it could be a contactor problem.
    Thermostat sends 24 volts to Contactor coil, completeing power from panel to both.
  • May 23, 2009, 07:25 AM
    KC13
    The outdoor disconnect may contain fuses. Have you checked?
  • May 23, 2009, 07:58 AM
    Stratmando

    Still need to know if compressor fan is working.