  • May 15, 2009, 05:06 PM
    terry63801
    Outside ac not running
    My ac been running fine but today I noticed started warming up in the house went outside the unit is not running but the fan in the house is any ideas the fan on the unit try to kick on but like it is low volt
  • May 15, 2009, 05:34 PM
    Stratmando

    Since inside Fan is working, so is transformer.
    Check for 24 volts to Outside Contactor coil. Verify 240 to Line side of contactor.
    You should have 240 volts on Load Side of the contactor when energized.
  • May 16, 2009, 07:26 AM
    Joshdta

    Check your start capasitor outside for burnt wires or a swollen top.
  • May 16, 2009, 02:04 PM
    terry63801
    Thanks guys I got it thanks for the help
  • May 16, 2009, 02:06 PM
    Joshdta

    What did it end up being?
  • May 16, 2009, 08:08 PM
    terry63801

    Capasitor thanks