Replaced themostat with same style. Still no 25v AC to outside unit. Contactor does not pull in, transformer is very hot. RC and RH terminals are jumpered.
![]() |
Replaced themostat with same style. Still no 25v AC to outside unit. Contactor does not pull in, transformer is very hot. RC and RH terminals are jumpered.
There is this guy that I am in love with I want to know if he feel the same way about me
Sounds like love is in the air with the previous poster. What type of system(heatpump or gas furnace) what make of system(Rheem, Carrier,Trane,Lennox) And the most important question is how did the old thermostat wire up?
tixie, just ask him, or post your question under relationships.
Car, please answer t-tops questions and we will try to help.
How and where did you jumper the wires. Try jumping them at the funace between r and y. let us know what you find. Also, if you have a volt meter, check to make sure there is not 24v at coil on contactor outside.
OK, you should be jumping r and y, instead of w and y. try this.
Go to the thermostat open the cover do you see a red wire and a yellow wire jump it that will start the unit outside. Red wire is your hot or 24 volts yellow is your cooling and green wire is your fan and white is your heating.. note one thing safey is frist... www888aizeoffilter.com
Some coleman units used a 3 wire setup and had a change over at the furnace, this may be your problem. What kind of t-stat was your old one?
You have two seprate units? Then the jumper needs removed.
OK, no problem, if the ac and the furnace are 2 seprate blower then remove the jumper between rh and rc
Then you may have triped a reset or blown the transformer on the ac unit. You have the furnace wired to rh and w and the ac wired to rc and y?
Yes that's correct. The jumper was in there with the previous thermostat which was the same as the new on
What is the purpose of the transformer in the ac unit before the contactor? By the way thanks for all the help.
To power the ac unit. So just so I am clear on what you have. You have a furnace inside? And a package unit out side with flex duct under the trailar to supply the air for ac?