  • May 10, 2009, 06:04 PM
    car9172
    Outside unit does not turn on
    Replaced themostat with same style. Still no 25v AC to outside unit. Contactor does not pull in, transformer is very hot. RC and RH terminals are jumpered.
  • May 10, 2009, 06:44 PM
    tixie

    There is this guy that I am in love with I want to know if he feel the same way about me
  • May 10, 2009, 07:36 PM
    T-Top
    Sounds like love is in the air with the previous poster. What type of system(heatpump or gas furnace) what make of system(Rheem, Carrier,Trane,Lennox) And the most important question is how did the old thermostat wire up?
  • May 10, 2009, 07:44 PM
    mygirlsdad77

    tixie, just ask him, or post your question under relationships.



    Car, please answer t-tops questions and we will try to help.
  • May 11, 2009, 02:44 PM
    car9172
    Quote:

    Originally Posted by car9172 View Post
    Replaced themostat with same style. Still no 25v AC to outside unit. Contactor does not pull in, transformer is very hot. RC and RH terminals are jumpered.

    It is a Coleman SCS 2 used in mobile homes. Unit worked fine earlier this year, thermostat smelled burned so I replaced it. I also jumpered the wires to send 25v to outside unit, contactor did not close.
  • May 11, 2009, 03:14 PM
    mygirlsdad77

    How and where did you jumper the wires. Try jumping them at the funace between r and y. let us know what you find. Also, if you have a volt meter, check to make sure there is not 24v at coil on contactor outside.
  • May 11, 2009, 03:30 PM
    car9172
    Quote:

    Originally Posted by car9172 View Post
    Replaced themostat with same style. Still no 25v AC to outside unit. Contactor does not pull in, transformer is very hot. RC and RH terminals are jumpered.

    I jumpered w and y at the thermostat. There is no voltage on the coil of the contactor. Not sure what you mean about furnace. Wires from thermostat-- one goes to coil the other goes through a transformer then to the other leg of coil. That trnsformer is very hot.
  • May 11, 2009, 03:41 PM
    mygirlsdad77

    OK, you should be jumping r and y, instead of w and y. try this.
  • May 11, 2009, 03:47 PM
    car9172
    Quote:

    Originally Posted by car9172 View Post
    Replaced themostat with same style. Still no 25v AC to outside unit. Contactor does not pull in, transformer is very hot. RC and RH terminals are jumpered.

    I have RC, RH, W , and Y. RC and RH are are jumpered at the terminals as per the thermostat instructions.
  • May 11, 2009, 03:59 PM
    class 101

    Go to the thermostat open the cover do you see a red wire and a yellow wire jump it that will start the unit outside. Red wire is your hot or 24 volts yellow is your cooling and green wire is your fan and white is your heating.. note one thing safey is frist... www888aizeoffilter.com
  • May 11, 2009, 03:59 PM
    Joshdta

    Some coleman units used a 3 wire setup and had a change over at the furnace, this may be your problem. What kind of t-stat was your old one?
  • May 11, 2009, 04:09 PM
    car9172
    Quote:

    Originally Posted by car9172 View Post
    Replaced themostat with same style. Still no 25v AC to outside unit. Contactor does not pull in, transformer is very hot. RC and RH terminals are jumpered.

    This is a mobile home so wire colors are probably not normal. I have a what and red coming from transformer in furnace, and a what and red going to outside unit. Heating and cooling have separate fans.
  • May 11, 2009, 04:11 PM
    Joshdta

    You have two seprate units? Then the jumper needs removed.
  • May 11, 2009, 04:11 PM
    car9172
    Quote:

    Originally Posted by car9172 View Post
    Replaced themostat with same style. Still no 25v AC to outside unit. Contactor does not pull in, transformer is very hot. RC and RH terminals are jumpered.

    The cheapest " Rite-Temp" they had at home depot
  • May 11, 2009, 04:13 PM
    Joshdta

    OK, no problem, if the ac and the furnace are 2 seprate blower then remove the jumper between rh and rc
  • May 11, 2009, 04:22 PM
    car9172
    Quote:

    Originally Posted by car9172 View Post
    Replaced themostat with same style. Still no 25v AC to outside unit. Contactor does not pull in, transformer is very hot. RC and RH terminals are jumpered.

    I removed the jumper reinstalled the thermostat turned to cool still nothing
  • May 11, 2009, 04:25 PM
    Joshdta

    Then you may have triped a reset or blown the transformer on the ac unit. You have the furnace wired to rh and w and the ac wired to rc and y?
  • May 11, 2009, 04:35 PM
    car9172

    Yes that's correct. The jumper was in there with the previous thermostat which was the same as the new on
  • May 11, 2009, 04:49 PM
    car9172

    What is the purpose of the transformer in the ac unit before the contactor? By the way thanks for all the help.
  • May 11, 2009, 05:12 PM
    Joshdta

    To power the ac unit. So just so I am clear on what you have. You have a furnace inside? And a package unit out side with flex duct under the trailar to supply the air for ac?