    I have a 200 amp panel with a 10/3 wire running to a shed, then hooked to a 110 receptable.
    My question is can I take the 10/3 wire and change the 110 circuit to 220 ?

    Thanks
    Dave
  • May 10, 2009, 03:54 PM
    stanfortyman
    What is a "220"?
  • May 10, 2009, 08:16 PM
    CIGARBOY50
    Quote:

    Originally Posted by stanfortyman View Post
    What is a "220"?

    from 110 volts to 220 volts !
  • May 10, 2009, 09:08 PM
    Missouri Bound
    Cigarboy, Stan is a stickler for telling everyone that there is no 220 anymore. But for your question, yes you can. Your 10/3 can safely handle a 30 amp, 2 pole breaker. You will need a ground from the panel to the outlet. I'll assume the ground wire is intact on the 10/3.
  • May 10, 2009, 10:01 PM
    stanfortyman
    Quote:

    Originally Posted by Missouri Bound View Post
    Cigarboy, Stan is a stickler for telling everyone that there is no 220 anymore.

    True enough, but also the fact that "220" is meaningless without knowing the amperage. It is a chronic DIY mistake to think that "220" is all that matters. Sorry for my intolerance.



    Yes, a 10/3 cable can be used for a 120v, 240v, or 120/240v circuit at 15, 20 or 30 amps.

    Typically it is used for a 120/240v - 30a circuit, such as a dryer or wall oven.