  • May 6, 2009, 03:43 PM
    boxsmart
    Waterheater very little hot water & dripping relief valve
    Hi, I have installed a new electric waterheater 100 Litres supply pressure 6 bars, pressure regulating valve set at 4 bars pressure relief valve 5 bars, when electricity switched on thermal expansion increases pressure to 8 bars, pressure relief valve starts leaking correctly at approx 5 bars but still pressure has increased to 8 bars. My problem- I have to adjust waterheater thermostat so as not have the relief valve leaking too much water (bucket full per week) due too thermal expansion thereby the 8 bars reading, although the water comes very hot approx 65 to 70 degrees centrigrade there is not enough hot water for two persons to have a shower. The pressure regulating valve is placed about 1.5 metre from waterheater. I am thinking of inserting an expansion tank would this help with above.

    Please help with a solution thanks
  • May 7, 2009, 03:34 AM
    hvac1000
    I am thinking of inserting an expansion tank would this help with above.

    The expansion tank properly installed should eliminate your problem. Follow the factory install instructions.
  • May 8, 2009, 09:38 AM
    boxsmart
    Quote:

    Originally Posted by hvac1000 View Post
    I am thinking of inserting an expansion tank would this help with above.

    The expansion tank properly installed should eliminate your problem. Follow the factory install instructions.

    Thanks for prompt reply I will procure an expansion tank if I can find an online seller in UK post & packing hopefully will be cheaper thanks again