-   -   Honeywell rth230b thermostat (https://www.askmehelpdesk.com/showthread.php?t=345946)

  • Apr 25, 2009, 11:48 AM
    banger
    Honeywell rth230b thermostat
    My thermostat works fine for the furnace but the air conditioner comes on outside but it don't blow or the fan is not working I put this thermostat in in fall of last year so didn't use the air
  • Apr 25, 2009, 11:53 AM
    Joshdta

    Did you put a jumper from rh to rc at the t-stat?
  • Apr 25, 2009, 11:54 AM
    Joshdta
    You say the outdoor unit comes on but not the indoor blower?
  • Apr 25, 2009, 11:55 AM
    banger
    Yes the jumper was already there
  • Apr 25, 2009, 11:56 AM
    banger
    An yes the unit outside comes on it just don't blow inside
  • Apr 25, 2009, 11:57 AM
    Joshdta

    OK sounds like you have a bad cooling fan relay. At you furnace. Does your furnace have a control board in the blower compartment?
  • Apr 25, 2009, 11:58 AM
    banger
    I couldn't tell you I am not familier with heating an air
  • Apr 25, 2009, 12:00 PM
    Joshdta

    OK, no problem. Do you have a volt meter of any kind?
  • Apr 25, 2009, 12:01 PM
    banger
    The guy that works on my heating an air told me last night about the yellow an green wire to the thermastst turns the fan reley on he's working now I am just trying to figure it out myself keep the wife happy lol
  • Apr 25, 2009, 12:03 PM
    banger
    Well I did have 1 but it got broke by my daughter
  • Apr 25, 2009, 12:06 PM
    Joshdta

    Well if you turn your fan switch to on does the fan come on?
  • Apr 25, 2009, 12:09 PM
    banger
    I know I had it wired up right according to the diagram
  • Apr 25, 2009, 12:09 PM
    banger
    I will go check an see if fan comes on
  • Apr 25, 2009, 12:13 PM
    Joshdta

    OK sounds like it is wired right. I think the problem is going to be at your furnace
  • Apr 25, 2009, 12:15 PM
    banger
    With heat an cool off the fan does not come on with it turned on to fan
  • Apr 25, 2009, 12:18 PM
    Joshdta

    The you either have a bad fan relay at your furnace. Or the green wire is broke or not touching at the t-stat. I would check the green wire at the stat first
  • Apr 25, 2009, 12:19 PM
    banger
    OK I will do that
  • Apr 25, 2009, 12:23 PM
    Joshdta

    If that is not the problem we can go from there.
  • Apr 25, 2009, 12:25 PM
    banger
    Well it must be the fan relay unless like you said the wire is broke somewhere where I can't see it
  • Apr 25, 2009, 12:26 PM
    banger
    But the furnace worked all winter long