Originally Posted by
tkrussell
Correct, you will not find a 200 amp panel that can have a 150 amp branch circuit breaker.
All I can think of is change the 150 amp panel in the home to a new 200 amp, and install a 2 pole 50 amp breaker in that to feed the garage.
Doing what you propose at the meter may be possible, the lugs would need to rated for two conductors for each leg. Then there would need to be two breaker or fuse disconnects, one 150 amp rated and another at 50.
There are 200 amp meters that contain two distribution breakers, but what I find is limited to 125 amp.
I think my solution is the simplest, but that is for you to judge.
Before purchasing any meter trim, you should consult with your power utility as each utility has their own requirements and allowed list of meter trims or equipment.
And consultwith both the utility and the local inspector to confirm what your plan is, esp if you want to split the meter into two feeders.