In my main panel, I have two 100 Amp incoming breakers. Does that equate to 200 Amp service?
![]() |
In my main panel, I have two 100 Amp incoming breakers. Does that equate to 200 Amp service?
Do you mean a double 100A breaker? Two breakers with the handles tied?
If so then no, this is a 100A service, not a 200A.
Something sounds strange.
Can you provide a picture?