  • Apr 22, 2009, 02:34 PM
    RodButler
    Relief Vent Requirements
    The plumbing code is boggeling me. In a single story slab on grade warehouse with long underslab waste piping runs, are relief vents required at 100' intervals?
  • Apr 22, 2009, 03:38 PM
    massplumber2008
    Hi Rod:

    In my code book... you are not required to install relief vents unless piping over ten branch intervals in a multi. Story building.

    You are required to install a cleanout every 50 feet for 3" and smaller and every 100 feet for pipe 4" and above.

    Let me know if you have questions...

    MARK
  • Apr 22, 2009, 09:30 PM
    Milo Dolezal

    I don't think you they are "relieve vents" . I think they are Clean Outs. In my area, you are required to install Clean Out every 75' feet.
  • Apr 23, 2009, 04:44 AM
    speedball1
    My code calls for cleanouts on a 4" building main to be 50 feet apart and 100 feet for lareger pipes. 4" house sewers shall have cleanouts installed every 75 feet and a clean out installed at every change of direction greater then 45 degrees.
    Cheers, Tom