    roughwater
    Can 220v-1 phase table saw be powered from a dryer outlet
    Hi
    I have a Delta 3 HP -220 volt single phase table saw in my garage but do not have a 220 volt outlet in the garage. I was considering making an extension cord to run from the garage to the nearby laundry room where I could plug into the 220 volt clothes dryer outlet.
    The dryer has a circuit breaker rated at 30 amps. The table saw motor is rated 12.4 amps.
    Could there be damage to the motor?
    Thanks,
    Brian
  • Apr 21, 2009, 05:03 PM
    KISS

    You could.

    If the saw contains a thermal or an integral starter with overloads, then your fine.

    If this is for occaisional use, then your fine.
  • Apr 21, 2009, 05:25 PM
    Fr_Chuck

    What is the amperage of the saw and how long is the extension cord
  • Apr 21, 2009, 05:39 PM
    KISS

    His post said 12.4 AMPS.

    Which makes the extension cord at least 14 AWG. 12 AWG may be preferred.

    Good point!
  • Apr 21, 2009, 05:39 PM
    roughwater
    Hi Fr_Chuck
    The saw motor is rated at 12.4 amps and I was planning on a 40-50 foot extension cord.
    Thanks
    Brian
  • Apr 21, 2009, 05:47 PM
    roughwater

    Thanks KISS
    How can I determine if the motor has a thermal or an integral starter with overloads?
    Brian
  • Apr 21, 2009, 05:56 PM
    KISS

    Thermal: Look for a red button on the motor

    Overloads: Look where the power cord goes

    Motor starters are always a good idea. They allow the motor to have an instantaneous overload for starting purposes.

    There are two types now. One has thermals that are selected by the FLA (Full load amps) of the motor and the other that's electronically adjustable.

    Generally they are used for 3 phase systems, but single phase is available.

    Sometimes they contain an integral start/stop switch and a lockout (padlock in off position) mechanism.