Originally Posted by
Milo Dolezal
Based on your response in #11, it appears to me your problem is your gas supply. You simply don't have enough gas to run all 3 heaters at the same time. Your heater will slow down water flow since it doesn't have enough gas to heat up all the water to the required temperature. I am sure if you turn up your temperature on all 3 heaters to 140F - you will get only trickle from the hot water side in your shower.
Adding one Rinnai to the existing house gas system almost always presents us with problem. Some upgrades are almost always required to assure proper operation of the new heater and not to cut down gas supply for rest of the house. In your situation, you have 3 (three) Rinnais.....
It appears to me your installer didn't want to mess with new gas system which is labor intense and could very costly - so he simply moved gas regulator closer to the heaters figuring he will bring unreduced gas pressure all the way to the gas fixtures - and than he would just ran 24" of gas pipe to supply the heaters itself. Besides, moving pressure regulator away from the gas meter is dangerous as well as it is a gross Code violation - at least in my area.
Also, you will most likely have to have your gas meter upgraded to at least 2" meter or even bigger. I would call your gas company and presented them with total number of gas demand (measured in Btu's) for the entire property including pool, spa, the 3 Rinnais, BBQ's + your house. Adding 600,00 Btu's / 550 cfm to your existing house gas system is a major addition that will certainly have negative effect all other gas fixtures in your house.