  • Apr 15, 2009, 01:28 PM
    fighterace26
    Montgomery ward 700 furnace "thermostat wiring"
    Old one has the standard Y, G, and Y,

    Then there is a W1 and W2 don't know where to put them

    This is just a plain jane furnace with an aftermarket central air unit,

    Everyone is telling me it must be a heat pump or two stage unit... I highly doubt it.

    Thanks in advance for any help.
  • Apr 15, 2009, 01:29 PM
    fighterace26

    I meant R, G, and Y,
  • Apr 15, 2009, 02:36 PM
    Joshdta

    R is for power, g is for fan, y is for cooling, w1 is for heat. The w2 should not do anything
  • Apr 15, 2009, 02:37 PM
    Joshdta
    You have 6 wires hooked up now?
  • Apr 16, 2009, 05:33 AM
    fighterace26
    Quote:

    Originally Posted by Joshdta View Post
    you have 6 wires hooked up now?

    No 5

    The old thermostat also Montgomery Ward has R, G, Y, and W1 and W2

    W1 and W2 if I follow them to the furnace they hook up to a transformer labeled W1 and W2

    The R G Y all hook up to a second separate transformer inside the furnace

    It looks like in the old thermostat that W2 jumps back to R via an internal switch that looks like it never moves?

    I will try without W2 and see what happens.
  • Apr 16, 2009, 06:07 AM
    Joshdta

    That's what I would do first. Then let me know what happens.