One of my customers has a problem which has me baffled. He has two gas fired, 40 gallon hot water tanks, connected in series (6 years old). They are turned up just one 'click' from the highest setting. Normally when a tank is turned up this high the water is boiling hot, but in this case it was just comfortable. When I left a couple of hot water taps running the hot water seemed to run out quite quickly (considering its two forty gallon tanks)
I am unsure which path to follow for the repair. Part of me is saying that it's the thermostat on the primary tank which isn't working, therefore pumping colder water in the secondary tank. Also, I'm thinking it could be the dip tube on the primary tank? The tanks are 6 years old so the dip tubes shouldn't have decomposed.
Any suggestions?
Thanks in advance:)
Went back there tonight and checked the temp at the drains with my digital thermometer (I tried this on the tank in my home first so I could compare readings) Readings were good. I then checked the dip tubes which were also fine. There was definitely heat loss between leaving the secondary tank and arriving at the faucets, but the basement was immaculately finished so I couldn't investigate any further.
I increased the temperature on the secondary tank a little bit higher. Even though both tanks are set quite high, I figure that the secondary one doesn't fire as often, so increasing it should give an extra few degrees. Perhaps a 50 gallon tank further down the line might be in order.
Thanks for the tips folks, I can now troubleshoot a basic tank blinfolded, now I just have to figure out the power vented beasties... whole other nightmare! I'm sure I'll be on and off here quite a bit, and I'll try and rattle the odd tip jar along the way.