    Air Circuit Breaker Trip Unit malfunction
    Masterpact M16H1 ACB, with STR38S Trip Unit. In=1600A.
    I'm aware that the trip unit may not function correctly while detecting currents below 20% of rated current. But my specific question is, could these conditions while causing the STR38S Trip Unit to malfunction, actually cause the unit to trip. As an example, chosen settings Io x In x Ir = approx. 1414A. With average amps per phase at approx. 80A, it is accepted that the Trip Unit may not follow the current/time curve settings. But could these conditions contribute to the unit tripping?
  • Apr 18, 2009, 09:23 AM
    sathe1963

    Malfunctioning of processor. Local heating if any to be detected... recommended before replacing.
  • Jul 12, 2009, 06:46 PM
    tigert
    Should be refreshed the unit. The new version soft can solved the Malfunction.