  • Apr 3, 2009, 08:29 AM
    meverett31
    Sub-panel install
    I'm installing an 8.1 kW solar system and running two inverters. My hope is to run both inverters to a sub-panel and move a few basic home breakers into the sub-panel. Since the Utility company wants me to install an AC Disconnect, I would like to install it between my sub-panel and the main. This will allow them to disconnect my solar power from the grid and hopefully leave me with basic lighting in the house if they do.

    First question - any issues with this approach?
    Second - If that works what size AC-Disconnect do I need? My sub-panel is 100 amps, pluggerd into 100amp breaker in the main.

    Appreciate any help thank you!
  • Apr 3, 2009, 09:08 AM
    meverett31
    I purchased the following, but since it's only 60 amps should I return and go with something like a 95amp?

    Quare-D DU222RB Safety Switch Square-D DU222RB Safety Switch 250V/Outdoor, 60A, 2 Pole No Fuse

    Thanks for the information
  • Apr 3, 2009, 02:31 PM
    Missouri Bound
    Hmm. If you are going to move a few circuits to the sub panel, then they won't be connected to the utility company any more... correct? If I am reading what you are saying correctly, your solar system will be independent of the utility company. If that is correct, you do not need any disconnect, since they aren't connected.

    Am I missing something?
  • Apr 3, 2009, 02:35 PM
    meverett31

    The Sub-panel is connected to the main. But the utility company would like the ability to disconnect my solar from the grid when they are doing repairs. At night when solar is not producing power I would be pulling from the Grid.
  • Apr 3, 2009, 02:38 PM
    Missouri Bound
    OK... that makes sense. There is a device called a transfer switch, which is designed when installing a generator. Their operation interlocks the two sources so that either the generator or the utility company is supplying power... but never both at once. Would this fit your application?
  • Apr 3, 2009, 02:46 PM
    meverett31

    Good question, this is where my lack oh knowledge comes in. My hope was to just place 100 amp AC Disconnect switch between the Main and the Sub. Something that the utility company could just walk up to and switch to off and lock it. I've seen a Square D DU323RB that appears might work.
  • Apr 3, 2009, 02:59 PM
    Missouri Bound
    What size breaker feeds your sub-panel? The breaker serves as disconnect.
  • Apr 3, 2009, 03:04 PM
    meverett31

    It's 100 amp breaker. The manual states that the utility company requires an AC Disconnect between a grid-tie inverter and the AC load center, close to the AC service entrance, with a visible and lockable handle.
  • Apr 3, 2009, 03:06 PM
    Missouri Bound
    You're on the right track with the disconnect. Just purchase one (non - fused) that's rated equal or higher to the circuit breaker.
  • Apr 3, 2009, 03:07 PM
    meverett31

    Great thanks!