    Day&night furnace ignites burner then shuts off
    Hi,

    I am trying to determine which part to replace on my 1989 day and night furnace.

    The furnace igniter lights the pilot when the t-stat calls for heat (I bypassed the t-stat to make sure the problem was not with the tstat by putting a jumper between the red and white to call for heat). Next the burner lights for a few seconds then it shuts down.

    What would be the most likely part to replace? Ignition module or some sort of limit switch? Your advise would be greatly appreciated!

    Thanks in advance,


    Greg.
  • Mar 28, 2009, 11:57 AM
    hvac1000
    1 Attachment(s)
    If it has one of these then the problem could be this part. You should really test if possible before replacing.
  • Mar 29, 2009, 09:00 AM
    gregroberts2009

    Hi,
    Thank you for the very helpful image! That's the part I thought. Thanks again for your help on this!
  • Mar 29, 2009, 10:43 AM
    hvac1000
    No problem