Originally Posted by
ballengerb1
There is little chance that this plumbing is original so its a guess as to when it was installed and what codes were followed. Do you see a vent stack or stench pipe exiting above the roof? If so I'd start by rodding that line with a sewer rodder. Use enough snake to reach roof to basement plus 20' more. I would alos remove fixture traps and rod into the lateral lines running into the wall. You need a much smaller snake for this, something like a 1/2' drum auger. The bubbling tells me you vents are clogged but probably everything is a little constricted too.