Verifying Grounding Connections
I recently rewired my basement workshop. I put in a short section of EMT to carry wires from the overhead joist down to a two-gang receptacle box and then out again to second two gang receptacle box. I ran two circuits so I could control which tools were on which circuits more easily.
I wire-nutted all of the ground conductors together (I ran 12-2 NM - probably should not have but it less than 6 feet total and open at the top)... I also pig tailed the grounds to each of the receptacles in both boxes and I pigtailed to a grounding screw in each EMT box.
So besides running 12-2 in conduit (which I found after I did it that I wasn't supposed to), I am curious how best to test that I have properly grounded the EMT.
I run test lite with one prong in the hot slot on one of the receptacles and the other prong touching the junction box. I get a lit (which I expected) but it did not trip the breaker. I would have thought that the prong-connection for the lit tester would have energized the conduit, which was (hopefully) properly grounded, and that would have tripped the breaker.
So (a) should it have tripped the breaker and if it should have (b) is my ground setup incorrect or is my breaker bad?