  • Mar 15, 2009, 04:56 AM
    jubabean
    Installing RTH6300B with wires that are not labeled
    I am trying to install a programmable thermostat (Honeywell RTH6300B) to replace an existing round Honeywell non-programmable thermostat. The wires on the existing thermostat are not labeled and there are only 2 wires attached (green and yellow). There is a red wire that is taped off. The new thermostat has terminals for about 6 different wires, but I am not sure where to put the existing wires. I tried to just match the colors (G and Y) but the thermostat is not responding. Any help would be appreciated.
  • Mar 15, 2009, 09:00 AM
    KISS

    Without me looking up the terminals and assumin that this is a heating only stat and not one for a mobile home where heat/cool is sselcted at the furnace and a common terminal is not required on the new stat then:

    If there is an Rh and Rc then use Rh, otherwise use R on the new stat.

    Use W instead of the Y terminial on the new stat.

    Post the new terminals or a link to the manual of the new stat.
  • Mar 16, 2009, 07:38 AM
    jubabean

    Perfect! R and W worked. Thanks so much!