    I energize a Y-Yn transformer 13.8kv/380/220. At no load
    all line to line voltage at the secondary were 380v but L1-N=215, L2-N=209 and L3-N=218 any one can explain me what is the cause of these unbalance voltage?? Ty..
  • Mar 23, 2009, 08:03 AM
    sarnian
    Hello danar

    Seems a case where the transformer is not properly balanced, which caused the neutral to move slightly from the nil position. Did you also test the voltages under equal loading? Same result?
  • Mar 23, 2009, 09:07 PM
    danar

    Yes I connected a three phase load but same result. Somebody advise me to ground the neutral on the primary side but there is no neutral bushing in the primary..
  • Mar 23, 2009, 09:24 PM
    sarnian
    Hello danar

    As you have a Y-Yn transformer there is no need for a primary neutral!
    The problem is in the transformer itself.
    Do you expect problems from using the available 215V, 209V, and 218V ?
    That's all within 2½% of the proper neutral point.
  • Apr 19, 2009, 06:09 AM
    sathe1963
    Once request to check ratio test of the transformer. If OK, ground neutral point on secondary side directly or through ngr according to the rating of the transformer.