  • Mar 10, 2009, 04:50 PM
    luckyrabbit7
    Laundry stand pipe #3
    I hate to be a pain with this question, but I would really like to get a few thumbs up
    Before I put this in. Any feedback would be great Thanks Jim
    http://farm4.static.flickr.com/3638/...f675d2.jpg?v=0

    http://farm4.static.flickr.com/3601/...5303d1.jpg?v=0
  • Mar 10, 2009, 04:59 PM
    ballengerb1

    I'd make that new TEE a new Wye. I am also pretty sure the new 2009 plumbing code now calls for your new drain to be 3", not 2". The shape of your plan looks fine and I will see if the code has gone into effect, you are likely OK with 2"
  • Mar 10, 2009, 05:03 PM
    massplumber2008
    Hi Lucky... Refresh your screen in 10 minutes. Finally answer this question...

    Thanks...
  • Mar 10, 2009, 05:10 PM
    ballengerb1

    OK the 2009 code is in print but I am not buying a copy at over $100. Call your building department and ask what code they are accepting in your area. They will likely still go with the previous code.
  • Mar 10, 2009, 05:38 PM
    massplumber2008
    1 Attachment(s)
    Hi again... sorry it took so long to post an answer to this one. I thought Milo got it!

    Anyway, Ballenger has proposed a 3" drain here. As he has also suggested, until he can confirm that this code has actually passed somewhere stick with the 2"... I am sure you will be fine.

    This is an involved answer. I don't use a double wye/45 combo. fitting here. I might use a double sanitary tee, but not a double wye/45 combo... and even then if clog occurs in drain line it is difficult to snake the drain as most of the time the snake ends up crossing the sanitary tee fitting instead of going down the drain... can be a pain.

    What everyone is concerned about here is venting each fixture. I would prefer to see you pipe this as presented in my drawing below. Here I use individual sanitary tee fittings ( the 2" sanitary tee fitting is not pointed too, but is present) and run a separate vent for the washing machine... connects back into sink vent as drawn.

    Otherwise, if your area permits a double wye/45 combo. fitting may work best..?

    Let me know what you think here...

    MARK
  • Mar 11, 2009, 03:59 PM
    luckyrabbit7

    Mark
    I'm going with your diagram, I'll let you know how it turns out.
    Thanks Jim
  • Mar 11, 2009, 04:10 PM
    massplumber2008
    Let me know if you have questions...

    MARK
  • Mar 11, 2009, 04:29 PM
    massplumber2008
    Hi...got your email. Thank you very much! I'll write you back tomorrow. Thank you again!
  • Mar 12, 2009, 11:25 PM
    luckyrabbit7
    I'll post a picture, once its in
  • Mar 13, 2009, 06:36 AM
    massplumber2008
    Thanks... and I'll answer your email as soon as I get a minute!
  • Mar 13, 2009, 07:41 PM
    luckyrabbit7
    Here's the dry fit. I did it like massplumber2008 lay it out , except for where the vent ties in. He said to go with 48" above finished floor. This is more like 66 ".
    If I don't hear anything back, I'm going to glue it up.
    Thanks Jim


    http://farm4.static.flickr.com/3664/...cc7e4c.jpg?v=0
  • Mar 13, 2009, 07:47 PM
    ballengerb1

    " going to glue it up" and prime it I assume. Looks good to me, how about you Mark?
  • Mar 14, 2009, 05:09 AM
    massplumber2008
    Hi Jim:

    I'd prime/cement it up as it is as well...nice job!
  • Mar 15, 2009, 01:53 PM
    luckyrabbit7
    Everything is hooked up, and I did 5 loads of laundry. There were no leaks and the stand pipe drained out just fine. So I put up the drywall.
    I just wanted to thank everyone for their input. I learned a few thing along the way.
    Thanks Again
    Jim
  • Mar 15, 2009, 07:24 PM
    ballengerb1

    We are now sending you an invitation to the Plumbers Ball, welcome aboard Jim.