  • Mar 8, 2009, 05:52 PM
    ed72073
    Carrier trouble codes
    Hi I am having an issue with a Carrier furnace model #58STA90. It will not light and it gives a code of three short flashing led lights and then one long. I checked the igniter and did not see any cracks across it.
  • Mar 8, 2009, 10:36 PM
    hvac1000
    31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than five minutes,
    inducer shuts off for 15 minutes before retry. Check for: - Excessive wind
    - Proper vent sizing - Defective inducer motor
    - Low inducer voltage (115VAC) - Defective pressure switch
    - Inadequate combustion air supply - Disconnected or obstructed pressure tubing
    - Low inlet gas pressure (if LGPS used) - Restricted vent
    If it opens during blower on-delay period, blower will come on for the selected blower off delay

    See your manual on the link below. Page 44 figure 50.

    http://www.docs.hvacpartners.com/idc.../58st-18si.pdf