I am running new 3" pvc toilet drain 4' between joist, then have an elbow, then have to cut 4' hole through 3 joist, to drain to 1st floor . Will I have a problem with the toilet draing.
Also, will 1' 1/2" vent be enogh for toilet?
![]() |
Hi,
I am running new 3" pvc toilet drain 4' between joist, then have an elbow, then have to cut 4' hole through 3 joist, to drain to 1st floor . Will I have a problem with the toilet draing.
Also, will 1' 1/2" vent be enogh for toilet?
Hi Gerry...
You said, "then have to cut 4' hole through 3 joist"...? Did you mean a 4" hole?. hope so... ;)
The toilet should drain fine as long as you have 1/4" pitch per foot of pipe and the vent connects into the toilet drain line within 6-8 feet of the toilet elbow.
A toilet requires a 2" vent, but 1.5" is better than no vent at all, for sure... so up to you here.
Let me know if you have more questions...
MARK