Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   Installing Honeywell HM506H8908 TrueSTEAM Humidifier 6 Gal Manual (https://www.askmehelpdesk.com/showthread.php?t=323811)

  • Mar 2, 2009, 01:18 AM
    ozzi1967
    Installing Honeywell HM506H8908 TrueSTEAM Humidifier 6 Gal Manual
    Hello
    I did installed the unit but it give me call service and when I do rest it blinks 7 times .
    All dip sitting are off
    I want the humidifier to run when the heat is on only
    I hooked up wire R from the humidfier to TR on the furnace
    I hooked up wire C from the humidfier to TH on the furnace
    I hooked up two wire running from the truesteam (hum) to the humidstat

    The furnace has TIME DELAY VALVE (V810A1012)
    And this delay has TR +TH and TR

    The furnace is lennox model G8 -120-1

    Any help
    Thank you

    --------------------------------------------------------------------------------
  • Mar 2, 2009, 04:44 AM
    KC13
    Check the furnace control board for accessory control terminal(s). Usually a designation of "H" or "HUM" indicates a provision for humidifier control. Assure it provides the correct voltage for your humidifier (if present). If no accessory terminals are present, you can install an Aprilaire AP-50 relay, wired in series with your current arrangement ("R" circuit) and clamped to the heating-speed blower motor lead wire. This will limit humidifier operation to heating cycles only.