Goodman Open Limit Switch
I have a Goodman GDS80904BNA downflow furnace that does not work. It is 3 years old. I am getting the open limit switch error code on the circuit board when the T-stat call for heat. Only the circ. Blower turns on and rans continuously until I turn it off.
Here is a little history on it. Once Every couple weeks this winter the furnace would act up. It would try to fire 3 times but it would not and shut down. A few minutes later it would start with no problem. Or it would start up and run fine for a few minutes but it would not reach the temperature. By the time I would call a HVAC tech it would be working and they told me there is nothing they could until they see it act up. This went on for 4 months. Finally last week it did this continuously for 1 day. By the time the HVAC tech got here the next day it would not even fire up. He replaced the gas valve and it worked good for about 2 days then it would turn off before it reached T-tsat temperature. It seemed to only do this at night. He came back and it worked fine, so he switched T-stats as a test, next night same problem. Now last night only the fan blower will run when heat is called for as stated above. I am waiting for repairman to come back.
Here is a few things I tested. I jumpered the primary limit, pressure switch, and rollout limit each one a time and I get the same open limit error code. I opened all dampers and registers on the supply side. Flame sensor has been replaced also. I don't think the Flue is blocked, but how would I check? Any ideas?