  • Feb 21, 2009, 01:50 PM
    hoopie033
    What is correct amperage for All electric Heat Stripps?
    What amperage are 15 kw heat stripps suppost to run at,, Right now they are running at 21 amp,, is that to high
  • Feb 21, 2009, 02:33 PM
    Perito

    Are you sure these are 15 KW strips? How about 1.5 KW strips?

    Power (watts) = volts * amps.

    15000 watts = 120 volts * A
    15000/120 = A
    125 amps = A (kind of high, I think).

    If it's a 240 volt circuit
    15000/240 = 62.5 amps

    If it were a 1.5 kw circuit
    1500 / 120 = 12.5 amps
    1500 / 240 = 6.25 amps

    If it's a 1.5 kw strip, and it's pulling 21 amps, it's probably faulty. It's too high regardless of the voltage being applied.
  • Feb 21, 2009, 02:49 PM
    KC13
    If you have a 15 kw heat package with three 5 kw strips at about 240v, 21 amps is about average (per strip).
  • Feb 21, 2009, 04:07 PM
    Perito
    5000 watts / 240 volts = 20.8 amps. That makes sense.
  • Feb 21, 2009, 06:10 PM
    KC13
    Quote:

    Originally Posted by Perito View Post
    5000 watts / 240 volts = 20.8 amps. That makes sense.

    As always, great minds think alike... ;)