I am installing a 200 amp pedestal that will feed a manufactured home, the house has a 200 amp box. The 200 amp pedestal is about 150 from the pedestal home. My question is what size wire do I need to use from the pedestal to the manufactured home?
![]() |
I am installing a 200 amp pedestal that will feed a manufactured home, the house has a 200 amp box. The 200 amp pedestal is about 150 from the pedestal home. My question is what size wire do I need to use from the pedestal to the manufactured home?
Id Refer You To The Electrical Dept At Home Depot! They Have A Chart That Will Answer Your Question.
#4/0 Aluminum URD cable is typical for this size service and distance. This type of cable is rated to be direct buried,usually in a trench 30 inch deep with 6 inch of sand below the cable and 6 inch of sand on top of the cable, then backfill with the natural material up to grade level.Also need a warning tape above the cable 6 - 12 inch below grade.
Assuming the main breaker is at the meter, then 4 wire cable is needed.
URD (Undergound Residential Distribution)cable, will consist of two black #4/0 wires for the hots,one #2/0 for the neutral and a #4 for the equipment ground.
Any section of the cable's path under pavement will require a conduit sleeve under the paved area, usually 3 inch PVC Sch 40 or DB conduit.
Hello my name is Derek from stoner electric INC you asking what size wire.. well it would be a 4awt 4 wire if you have any more you are not in the range for voltage drop so you don't need any other size? s you can reach me at my email address [email protected] thanks and have a nice day..
I would use 3/0 copper. Not sure where in Florida you live, but in our county, aluminum not allowed, Salt air and corrosion. If aluminum is allowed. Use No-Ox type product
For connections.