  • Feb 4, 2009, 07:27 PM
    daleeubanks
    The Flame goes out
    In the gas furnace, is it normal for the flame to ever go out when the fan is on?
  • Feb 4, 2009, 07:42 PM
    hvac1000
    Yes under the correct circumstances. The flame will go out then the blower will keep blowing till all the residual warm air is out of the furnace. Now if the flame goes out while the thermostat is still not satisfied that could be a problem with the furnace.
  • Feb 4, 2009, 07:50 PM
    daleeubanks

    That's what's happening. I takes a while for the thermostat to be satisfied. We may have to kick it up way high. This is an intermittant problem. I'm hoping I just have a bad thermostat. I already changed the batteries.
  • Feb 4, 2009, 07:58 PM
    hvac1000
    Intermittent problems are alweays the worst to figure out.
  • Feb 4, 2009, 08:00 PM
    daleeubanks

    Could it be the stat?
  • Feb 4, 2009, 08:08 PM
    hvac1000
    Yes it could be. It could also be other things like the furnace itself. Disconnect the R and W wire in the furnace and jump them together with a piece of wire. Then turn the power switch back on and let the furnace run. It it runs without turning off the burner flame then the problem is probably with the thermostst. If the burner cuts off then the problem is probably with the furnace.
  • Feb 4, 2009, 08:12 PM
    daleeubanks

    Ok, thanks, I'll try that a get back to you
  • Feb 5, 2009, 04:54 AM
    KC13
    Quote:

    Originally Posted by hvac1000 View Post
    Intermittent problems are alweays the worst to figure out.

    Brother, don't even get me started, I'm saving it for my book!:p