  • Feb 3, 2009, 01:53 PM
    jerryp40055
    i need to know the starting and running watts
    I have a nordyne e2eb-023hb all elec furnace. I am thinking of getting a whole house generator and I need to know the starting and running watts to size the genset. The label says it has 2 circuits 1-45.5 amps and 1-48.3 amps. I have 2 circuit breakers for the furnace each 60 amps. Both look to be 2 breakers connected together so that you turn them on and off together. I think this means that each breaker is 240 volts and I should multiply amps x volts to get watts. 10920 watts and 11592 watts. Is this correct? One genset sales place tells me I need 12kw just for the furnace and another says I need 24kw.
  • Feb 3, 2009, 02:17 PM
    KC13
    The circuit breaker sizes for the fan coil/heater package aren't an accurate gauge when sizing the load. Look for a voltage/kilowatt rating on the heater package label. Factor in an extra 1-2 kw for the blower and other components.