  • Feb 2, 2009, 03:41 PM
    Survivor6
    Finding older parts for Trane gas furnace?
    I'm currently looking for an in-line fusible link for an older Trane forced-air gas furnace. I've tried quite a number of places so far with no luck. One place I contacted said they could get it but wanted over $90 with shipping (absurd).

    Does anyone have experience with a good supplier of older furnace parts with reasonable prices? (I've seen this type of link go for $15-20.) Or maybe some of you experienced repairers could suggest a substitute link as a replacement. I don't know the limit temperature but it appears to just be a high temp safety limit for the wiring compartment.

    (The part no. if it helps, is WG23X62 for a BLU108E936B1 Trane furnace (108000 BTUH).

    Thanks for your help.
  • Feb 2, 2009, 04:33 PM
    wmproop
    This type of thing seem to happen a lot when a person owns trane equipment,, I wish you luck, someone might come along that can help you
  • Feb 2, 2009, 06:06 PM
    hvac1000
    That furnace is about a 1980 model and parts are hard to come by. Can you post a picture? Can you read any numbers off the device?
  • Feb 3, 2009, 02:05 PM
    Survivor6
    Hey, folks. After dozens of deadends on the internet and calling every local HVAC supply company within 30 miles, I finally found a very helpful gentleman with a couple of these flame rollout fuses in their warehouse. So much work but only $11, so a happy ending. :D

    Thanks for your thoughts and efforts.
  • Feb 3, 2009, 02:12 PM
    KC13
    Have you determined why the original failed, and corrected the condition? If not, the new one may fail in short order. If it is the device I am thinking of, it reacts to flame roll-out.
  • Feb 3, 2009, 02:12 PM
    hvac1000
    Glad you got it going.
  • Feb 9, 2011, 11:28 AM
    Survivor6
    Yes, you are correct. The original problem was caused by a blocked air filter which has been corrected. Link installed and all temps within spec. Thanks.
  • Nov 26, 2012, 05:57 AM
    waternwavs
    Can you please post the name, address and number of where you got the part? Thanks!
  • Nov 30, 2012, 10:12 AM
    Survivor6
    I obtained the fuses from Trane of King of Prussia. (610 – 962 – 1600). If they no longer carry them, you have two options. One is to find a fusible link from another manufacturer that opens at the same temperature. The one for this furnace (which is Fuse Assembly WG23X048) opens at 109°C (228°F). (The part number for the fuse in the kit was ASM – 218305779G11.) Your other option is for you to buy the spare fuse from me that I purchased at the time since I've had to replace my old furnace since then. Good luck.