    marabbot
    Only 3 out of 4 elements heat up in my furnace but all 4 are good?
    Only 3 out of 4 elements heat up in my furnace and all 4 are good what's wrong ?
  • Feb 1, 2009, 06:29 AM
    Stratmando

    If all are good, then it would be wiring, connections? Try swapping a good and a bad, then see which one fails, the same Element, or the same location?
  • Feb 1, 2009, 08:58 AM
    hvac1000
    One of your units heat sequencers is probably defective no allowing the one heater to come on.
  • Feb 1, 2009, 10:45 AM
    KC13
    How did you test the elements, to arrive at the conclusion that they are good? A clamp-type ammeter will reveal which elements are working, and a voltmeter will reveal where power is being interrupted to any that aren't. Heat relay/sequencer, power wiring, limit control, fusible link, broken heater string, or power supply/fuse/circuit breaker are the possible culprits. You may also check the control wiring for the possibility that the relay that controls the element in question isn't even hooked up.