Another bird in the vent? (Ignition Proving Failure)
Several days ago my gas furnace quit working unexpectedly during the night without any warning signs. It is a Carrier 58MXA100-16 manufactured in 2005, in service since 2007.
I get status code 34 “Ignition Proving Failure”.
Steps I went through in troubleshooting:
1. Turn heat on at thermostat.
2. Inducer motor runs until pressure is built up.
3. Igniter heats up until orange.
4. Gas valve connection goes from to 27.2-27.5 volts for several seconds and I hear a click.
5. I hear the hissing sound for the gas but see no flames.
6. Gas valve connections voltage drops.
7. Igniter cools down.
8. Steps 3-7 repeat three times and then the system goes into Ignition Lockout (code 14) as expected.
When I remove the burner box cover the gas ignites and the furnace operates properly. When I replace the burner box cover leaving a small gap for air to pass through, air gets sucked in through the gap with a good amount of pressure and the furnace operates. Heck, even having the screws loose on the cover allows the furnace to work.
This leads me to think there could be an obstruction in the inlet for the combustion air. I’m a little suspicious that’s it because (and you’ll love this story)…
When my furnace wouldn’t work when we first tried it for the winter a few months ago a tech came out and determined that the inducer fan was sticking a bit. He wiggled it and that was enough to get it working, though it was making strange noises and seemed stressed. Well, it stopped working again a few weeks later, so I suspected a clog and disassembled the inducer fan and found a dead rotting bird inside blocking the fan blades. Absolutely disgusting. Must have come in through the vent (outgoing combusted air). Needless to say I'm not calling that HVAC company again, and I'd like to try to solve it myself this time.
So now I’m wondering if something has got into the inlet for combustion air and is blocking it just enough that not enough air is being provided for ignition.
Other notes:
• Immediately before entering the furnace it branches to the water heater, which is working fine along with all other appliances in the house.
• I cleared the tube (for the gas valve that connects to the pressure sensor) of any moisture. There was a small amount of moisture, probably less than one drop.
• Checked the voltage of the rollout switch and the pressure switch. Both are fine.
• I verified that the two green/yellow wires are properly grounded with good contact.
• I know it is a common problem but I didn’t check anything related to the flame sensor since there is no flame, so I believe the problem is before that.
According to the manual, other possible issues:
• “Inadequate flame carryover or rough ignition.” – not sure how to check this
• “Low inlet gas pressure.” – doesn’t seem like the culprit here
• “Proper firing rate.” – not sure how to check this
• “Check for air leakage around igniter bracket.” – I don’t detect any leakage
Any ideas?
Any tips from you experts would be much appreciated!