How to calculate the short circuit current flow in a three phase circuit?
![]() |
How to calculate the short circuit current flow in a three phase circuit?
To calculate short circuit current flow in a 3 ph. Circuit, we should know % impedance of source like transformer or generator. Fault mva = base mva / % impedance. On obtaining fault mva, we could find out a.
In short:
If the impedance of the transformer is 5%
If the full load current of the transformer is 1000A
The short circuit current is 20 times the full load current
i.e. short circuit current = 20,000A
STC is maximum fault current that a system is designed to withstand.For obtaining STC it will be as following example.
Conider a 10 MVA transformer with 6.5% Impedance. System voltage is 13.8/4.16KV. Now Fault MVA = base MVA/PU Impedance
So Fault MVA=10/0.065=153MVA
Now Fault Current = 153*1000/(1.73*4.16)=21259A = 21KA
I hope this can help