  • Jan 26, 2009, 04:12 PM
    rfroemer
    No ignition of Bryant furnace
    Byrant 90% Model 399A furnace. The Blower works fine and the filter is clean. Once the furnace starts there is no ignition. Where do I start with the ignitor or the spark generator.
    Suggestions please.
    Ron
  • Jan 26, 2009, 04:25 PM
    KC13
    What "starts"? The draft inducer? If so, the next device in the operating sequence to activate is the pressure switch. If the inducer runs, but no spark/pilot flame, check combustion vents/drain hoses for blockage.