  • Jan 20, 2009, 06:58 PM
    pod215
    Installed a honeywell RTH7600B and the cooling and heating are reversing?
    My new RTH7600B when set to heat is cooling. Checked the wiring and settings to no end. What can I do?
  • Jan 20, 2009, 07:26 PM
    wmproop

    Sounds like you might need to look at wiring again,, how about the (should be) orange that goes to the reversing valve,, this assuming you have a heatpump
  • Jan 21, 2009, 10:15 AM
    dac122

    What was the old tstat, how did it energize the reversing valve, and what manufacturer do you have? Does putting it in cooling mode give you any heat?
  • Jan 24, 2009, 04:09 PM
    pod215
    Reset setting 190 to other setting and it worked.
  • Jan 26, 2009, 07:00 AM
    dac122
    Quote:

    Originally Posted by pod215 View Post
    Reset setting 190 to other setting and it worked.

    Excellent. Your RTH7600 is now energizing the O/B terminal in accordance with what your HP needs to turn on heating. It always helps to know what your equipment expects before embarking on a change of controlling equipment.