I have a Beckett AFG burner, the furnace is power vented and has a V1 head.
The burner starts up then after about 10 sec trips safety. I have replaced electrodes and nozzle, thoroughly cleaned head and air tube. Yesterday I had a service man come and adjust air using CO2 sensor and a probe to check conditions in pipe. He stated unit was running very close to perfect, yet a short time it started kicking again. He checked transformer voltage and stated it was good. The furnace was serviced 3 months ago but I know now that the electrodes were never changed so now I am wondering if oil filter was changed.
The furnace always stay on after I reset the safety switch.
Any suggestions on what to try?? I have set all mechanical specs according to Beckett manual... please help me
Thanks