Repost of grounding dilemma
Having received no replies to my request to review the thread, I would like to repost the original question. Readers, please note that there are two locations referenced here- a "main disconnect" and a "main panel." Both are currently grounded via driven ground rods but only the main disconnect has a bonded neutral. I would much appreciate some of the experts in this group responding to the questions herein.
I apologize that my original question was not perfectly clear. I am also well aware that the problems were caused by the failed neutral but in the process of replacing the "main" breaker panel I wanted to reevaluate my grounding system and upgrade it if advisable. Let's start over.
A main fused, 200A disconnect is fed via underground cable ( the one which failed). This disconnect is grounded via a driven rod. The first question is whether I should consider upgrading this ground by running a ground to a well casing which I will be able to do when the power company fixes their underground cable? (neutral bonded at this disconnect).
When originally installed, the main breaker panel in the house was fed with about 60'-70' of 3-wire service entrance cable run underground from the main disconnect. I believe this to have been a mistake as no ground was provided. Instead, a second ground rod was driven in a different location to ground this panel. Finally, when I constructed a garage, I ran a conduit between the main disconnect and the breaker panel. At present, there is #6 ground conductor in this conduit.
My electrician feels this ground conductor should not be used. If I wish to improve the ground at the main panel, he advises only driving a second ground rod. So this is the second question. Should I tie the main disconnect and main breaker panel grounds together with the #6 conductor or leave the breaker panel grounded only via the driven ground? If tying them together is a good idea, should I pull something larger in the conduit (#4?)? (reminder, neutral is not bonded in this panel as per code).
I believe it is true that using the ground in the conduit is actually a code violation because it is not "contiguous" with the conductors in the 3-wire cable. My goal is only to get the best ground possible.
I appreciate the significant knowledge of stanfortaman in his posts. My understanding is that grounding systems are primarily for safety purposes but at higher frequencies (above 60Hz) may also provide for signal references and lightning protection. In any case, I believe NEC requires grounds and, hopefully, with a low impedance to "earth ground." I am much less clear on the actual aspects of providing good grounds and it is not clear to me whether "better grounds" might have alleviated some of the wild voltage swings resulting from the neutral failure.