  • Jan 15, 2009, 07:30 AM
    mike0009
    York furnace gmp100-3
    My furnace won't stay running. The inducer motor kicks on but then shuts off. The control board light flashes 3 times telling me the pressure switch failed to close. I cleaned the hose and replaced the pressure switch since it was about 13-14 y/o. I also cleaned the opening to the inducer motor. I'm still having problems with the pressure. The inducer comes on and off now while the furnace is running and I'm getting the 3 flashes on the control board again.
  • Jan 17, 2009, 06:13 PM
    mike0009
    Ok. I replaced the control board and the furnace is working fine.
  • Jan 17, 2009, 10:32 PM
    hvac1000
    Glad you got it going