  • Jan 11, 2009, 11:08 PM
    stummped
    Day + Night furnace blower only comes on with no heat
    Hello and Happy New Year... We have about a 15 year old Day + Night furnace that only the blower comes on with no heat... Is there a way to test the limit switches? There is 4 of them in the furnace.. There is a small square button in the center of all of these switches.. I wanted to test these before we buy a circuit board... Thank you so much for any response...
  • Jan 11, 2009, 11:45 PM
    MarkwithaK

    Do you have an electrical multimeter?
  • Jan 12, 2009, 03:27 AM
    hvac1000
    There is a small square button in the center of all of these switches..

    Push the button in. If the switch is tripped pushing it in will reset it. Otherwise you can jump each switch out one at a time. If it starts working you cannot leave it jumpered since it is a safety device and must be replaced before you wuse the furnace.

    Posting a EXACT model number would be helpful.
  • Jan 12, 2009, 12:03 PM
    stummped
    Quote:

    Originally Posted by MarkwithaK View Post
    Do you have an electrical multimeter?

    HI and Thank you for the response.. Yes I do have a multimeter..
  • Jan 12, 2009, 12:05 PM
    stummped
    Quote:

    Originally Posted by maiden usa View Post
    I know nothing about this stuff, but eventually someone is going to suggest that you clean something called a flame sensor. I just thought I would tell you so you wouldn't be caught off guard.

    Thank you and I will clean that with sand paper..
  • Jan 12, 2009, 12:06 PM
    stummped
    Quote:

    Originally Posted by hvac1000 View Post
    There is a small square button in the center of all of these switches..

    Push the button in. If the switch is tripped pushing it in will reset it. Otherwise you can jump each switch out one at a time. If it starts working you cannot leave it jumpered since it is a safety device and must be replaced before you wuse the furnace.

    Posting a EXACT model number would be helpfull.

    HI.. The model is 376CAV060095 Thank you for the response...
  • Jan 12, 2009, 01:30 PM
    stummped
    Quote:

    Originally Posted by stummped View Post
    HI and Thank you for the response.. Yes I do have a multimeter..

    Can you tell me how to check them with the multimeter.. Thank you again for any response...
  • Jan 12, 2009, 05:28 PM
    KC13
    Quote:

    Originally Posted by stummped View Post
    Can you tell me how to check them with the multimeter..Thank you again for any response...

    Set the meter to measure voltage and apply probes to both sides of switch. If you read 0 volts, move on to the next one. If you read voltage (approximately 24v.) the switch is open.
  • Jan 12, 2009, 07:55 PM
    stummped
    Quote:

    Originally Posted by KC13 View Post
    Set the meter to measure voltage and apply probes to both sides of switch. If you read 0 volts, move on to the next one. If you read voltage (approximately 24v.) the switch is open.

    Thank you KC... I will put the meter on them.. Is this OK to do with the blower motor running? Thank you again for your response...
  • Jan 12, 2009, 07:58 PM
    KC13
    Yes, you need the system powered to perform this test.
  • Jan 12, 2009, 08:23 PM
    stummped
    Quote:

    Originally Posted by KC13 View Post
    Yes, you need the system powered to perform this test.

    Thank You Very Much KC... I will give it a try..
  • Jan 12, 2009, 11:43 PM
    hvac1000
    1 Attachment(s)
    Quote:

    Originally Posted by stummped View Post
    Thank you and I will clean that with sand paper ..


    Did someone say flame sensor?
  • Jan 13, 2009, 04:53 AM
    KC13
    Now that is just gratuitous. I would expect that sort of thing from Hollywood, but you? :D
  • Jan 13, 2009, 05:09 AM
    hvac1000
    1 Attachment(s)
    Did someone say Hollywood ? Lets go visit Granny.
  • Jan 13, 2009, 03:38 PM
    KC13
    773H yeah! Swimmin' pools, movie stars!
  • Jan 13, 2009, 10:46 PM
    stummped
    Thanking you kc, hvac1000, mark with a k and maiden for all your help... It works now..
  • Jan 14, 2009, 04:58 AM
    hvac1000
    Quote:

    Originally Posted by stummped View Post
    thanking you kc, hvac1000, mark wih a k and maiden for all your help... It works now..


    Good deal I new we were good for something. Stay warm.
  • Jan 14, 2009, 07:22 PM
    stummped
    Quote:

    Originally Posted by hvac1000 View Post
    good deal i new we were good for something. Stay warm.

    You folks are awesome!!
  • Jan 14, 2009, 08:39 PM
    Cat45
    Comment on stummped's post
    What was the solution??